Modifications to Conduit Fittings

Status
Not open for further replies.

mphymel

Member
I have observed several instances where the covers for 2 and 3" LB fittings have been drilled and tapped to facilitate the installation of drain fittings.

Some of these instances were done in classified areas (CL I Div 2).

Is this in violation of the code. If so, where is this stated. I have spent hours searching for a section which addresses this issue.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Re: Modifications to Conduit Fittings

Aritlce 230.53 allows raceways to be "arranged to drain". How this is usually accomplished, I don't know. I also think it is interesting that this is in Article 230 - Services. So can raceways other than the service conductors be arranged to drain? Again, I don't know. The hazardous location adds another complication.

Has anyone else ever arranged a raceway to drain?
 

tony_psuee

Senior Member
Location
PA/MD
Re: Modifications to Conduit Fittings

My experience with class listed conduit fittings is that they are listed as submitted by the manufacturer and any modifications voids that listing. I have always accomplished a drain point in the line by specifying a "T" fitting at the low point, or panel penetration with an explosion proof draing. More expensive because of the additional material, but clean. With what you had described, even if they are using an explosion proof drain, I would have to believe is in violation of code.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Modifications to Conduit Fittings

Class 1 Division 2 areas do not require explosion proof conduit fittings, unless the fitting has been installed between an enclosure that is required to be explosion proof and the seal fitting. The modification of the fitting is likely a violation of the listing for the LB.
Don
 

pierre

Senior Member
Re: Modifications to Conduit Fittings

225.22 Raceways on Exterior Surfaces of Buildings or Other Structures. Raceways on exterior surfaces of buildings or other structures shall be rain tight and arranged to drain. (quote from the 2002 NEC)

Pierre
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Modifications to Conduit Fittings

Originally posted by steve66:
Has anyone else ever arranged a raceway to drain?
I rewired a "Flume" ride and replaced all the rotted EMT with aluminum ridged.

At all low points I put an 1/8" hole for draining.

Most times this would be at an LB or box, I do not know if this would be a listing violation, but I do know water Always finds a way into raceways.

Bob
 