modifying contents of an Exd enclosure

bubu

Member
Location
Pittsburgh
Occupation
Engineer
Hello,

First of all, I'm mostly used to the European standards, so bear with me if this is a silly question.

I'm involved in a project where the contractors are wanting to replace the components within a certified Exd enclosure. Basically there's a little lcd display that they want to replace with an led one that can be networked rather than the RS485 one they have.

In Europe this is a no go since there's things like the temperature rating and the available internal volume which will be affected by the modification, but I'm told this isn't a concern when it comes to NFPA/UL requirements and I find it slightly odd. I don't have access to the UL1203 to understand the requirements but was wondering if someone can shed some light on this?
 
If one modified a listed item such as this panel the modification(s) would need to be approved by the AHJ.

Generally these kind of modifications are not an issue.

In any case, none of the IEC standards are used in US classified areas. We have our own standards. They can sound the same, but they are not.
 
If one modified a listed item such as this panel the modification(s) would need to be approved by the AHJ.

Generally these kind of modifications are not an issue.
Thank you so much for the clarification.

So, we'd need to find the AHJ for that area and check their requirements when it comes to altering Exd boxes.

In any case, none of the IEC standards are used in US classified areas. We have our own standards. They can sound the same, but they are not.

IEC standards aren't quite the standards we have to follow in Europe either, those are the ENs which although have very similar text are not at all the same.

My doubt with regards to this is really because of the protection concept relying on available internal volume and temperature within the enclosure.

Still, thanks for the clarification.
 
We design, build, and certify hazardous location power and control cabinets globally.
Per our hazloc certificate for North America, if the physical doesn’t match the drawing/documentation the field certification is void.
I’d check with the certifier.
When this scenario comes up, we evaluate the change in variables and if all requirements are met we update documentation and have one of our field techs make a site visit to install/support, etc.
I’m not sure if it’s just our certificate or if it’s an across the board standard, but someone from our team must perform the install.


Sent from my iPhone using Tapatalk
 
We provide class/div as well as ATEX and IECEx certified solutions.
My comments were from the perspective of a class/division North American solution.


Sent from my iPhone using Tapatalk
 