I've searched the code and the forum; I'm not sure about this, so here goes.
3 section modular building is being moved in next to hospital. Feeding the modular with a 400A and a 200 amp circuit from the hospital distribution panel which is 3 PH, 208V. Feed will be thru EMT across roof to gutter on top of modular. <continuous metal path between buildings> (200 - 2" C, 3/0's ; 400 - {2} 2" C, parallel 3/0's). This powers all of the lighting and 120V power in the modular. Each feed goes straight to main breakers on the respective load centers in the modular.
The Catscan and MRI are each fed seperately from seperate services not located in hospital building. Services are pole mounted about 200' away.
MRI - 480V, 3PH, 200A, PVC UG, 3/0, 5 wire.
CTscan - 480V, 3PH, 150A, PVC UG, 2/0, 5 wire.
Each 480 feed goes straight in the bottom of the modular to the main breaker on the equipment.
I'm confused about the grounding requirements; ground rods at modular for each feed? bonding? I can use all the help I can get.
3 section modular building is being moved in next to hospital. Feeding the modular with a 400A and a 200 amp circuit from the hospital distribution panel which is 3 PH, 208V. Feed will be thru EMT across roof to gutter on top of modular. <continuous metal path between buildings> (200 - 2" C, 3/0's ; 400 - {2} 2" C, parallel 3/0's). This powers all of the lighting and 120V power in the modular. Each feed goes straight to main breakers on the respective load centers in the modular.
The Catscan and MRI are each fed seperately from seperate services not located in hospital building. Services are pole mounted about 200' away.
MRI - 480V, 3PH, 200A, PVC UG, 3/0, 5 wire.
CTscan - 480V, 3PH, 150A, PVC UG, 2/0, 5 wire.
Each 480 feed goes straight in the bottom of the modular to the main breaker on the equipment.
I'm confused about the grounding requirements; ground rods at modular for each feed? bonding? I can use all the help I can get.