NEC314.28 states the 6X rule applies to conduit bodies as well as pull boxes.
We need to install 4- 600KCMIL ( THHN ) and #3 ground in a 4" EMT raceway. Would like to use 4" Mogul LB to transition out of electrical room.
6X rule for 4" conduit =24". Conduit body measures 28" total.
Any other considerations ?
Conduit body is stamped 866 cu in.
We need to install 4- 600KCMIL ( THHN ) and #3 ground in a 4" EMT raceway. Would like to use 4" Mogul LB to transition out of electrical room.
6X rule for 4" conduit =24". Conduit body measures 28" total.
Any other considerations ?
Conduit body is stamped 866 cu in.