Does anyone know of a code requirement that requires a mogul LB to be used on an Electric service?
Example: Can I pit 3 #3's in an inch and a quarter LB?
314.28 (A) (3) seems to say I can if I'm within the 40 percent fill of Ch. 9 Table #1. And if I'm not then it has to be stamped inside the LB what size wire and How many is OK.
Anybody got some references for me?
As an old wireman I know it's best to use what we used to call a service LB for ease of pulling and so small chance of damaging the cable. However, I'm looking for the proper code references.
Jim