NECA 111 for 2003 for the installation of non-metallic conduits in paragraph 4.1.m says, "Avoid moisture traps where possible. Where moisture traps are unavoidable, provide junction boxes with drain fittings at raceway low points." This statement has been incorporated into many project specs.
NEC 225.22 requires that raceways on exteriors of buildings shall be arranged to drain, and NEC 230.52 says that where exposed to the weather, raceways enclosing service entrance conductors shall be suitable for a wet location and arranged to drain. NEC 314.15 says that in damp or wet locations, boxes shall be placed or equipped so as to prevent moisture from entering or accumulating within the box and permits this installation of 1/4" or smaller drain holes or listed fittings.
The NEC references seem to apply to above ground installations. Is it correct to interpret NECA 111 4.1.m as applying to underground installations? Does it seem reasonable to require the installation of a junction box with a drain fitting in all underground conduit runs with 90s at both ends? In addition, would this NECA requirement justify requiring all underground conduits to be arranged to drain to junction boxes that aren't shown on the plans?
NEC 225.22 requires that raceways on exteriors of buildings shall be arranged to drain, and NEC 230.52 says that where exposed to the weather, raceways enclosing service entrance conductors shall be suitable for a wet location and arranged to drain. NEC 314.15 says that in damp or wet locations, boxes shall be placed or equipped so as to prevent moisture from entering or accumulating within the box and permits this installation of 1/4" or smaller drain holes or listed fittings.
The NEC references seem to apply to above ground installations. Is it correct to interpret NECA 111 4.1.m as applying to underground installations? Does it seem reasonable to require the installation of a junction box with a drain fitting in all underground conduit runs with 90s at both ends? In addition, would this NECA requirement justify requiring all underground conduits to be arranged to drain to junction boxes that aren't shown on the plans?