mstrlucky74
 - NJ
Whats the difference between molded case and 100% thermal magnetic breakers? Price higher on 100% thermal magnetic I believe. Thanks.
			Nope, except it would have to be a tested assembly, so the breaker only goes with that tested panelboard, not just any standard panelboard in their line.Is there any technological reason a manufacturer couldn't produce a MCCB that uses an electronic trip, that is 100% rated, and that can be used in standard panelboards without extra clearance to other circuit breakers? I'm assuming here that an electronic trip's trip curve wouldn't be affected by ambient temperature.
Well, here's my understanding, in case it helps you (and so someone can correct me if I'm wrong). It's all about limitations of standard breakers; a wire can carry current at its ampacity indefinitely without damage.I just don't follow the 125% rule![]()
So are these standard thermal-magnetic breakers, and does the the special panel construction mean more space between breakers?The Square D I-Line panel, from Schneider Electric, has the ability to be ordered with 100% rated branch breakers. But they are rarely worth the cost until you start getting into circuits over 400A (about the point where savings in material and labor outweigh the cost of the special panel construction).
It’s not necessarily just the trip unit that’s the issue though, it’s the ability of the entire breaker to dissipate heat. Most (if not all) breakers with ETUs can be ordered as 100% rated for the same price, but once it has that 100% rated label on it, your use of it becomes restricted. One of those restrictions will be that it must be mounted with limitations on what is next to it. Other breakers on either side will violate that.
A standard thermal-magnetic MCCB tested by itself (in an enclosure? in open air?) at 40C ambient is supposed to hold its rated current indefinitely. That's a spatial arrangement that maximizes the breaker's ability to cool off by rejecting heat to its environment. Under these conditions, the thermal trip unit will reach some steady-state temperature, due to an equilibrium between the self-heating from the current through the breaker and the breaker's heat rejection to the environment. The thermal trip unit is calibrated to not trip at this steady-state temperature (but presumably to trip at a temperature just a bit higher).
Now take that same breaker and put it in a panel full of other breakers. The nearby breakers inhibit any convective cooling off the case of the breaker, plus the nearby breakers are themselves heat sources, so their temperature may be higher than ambient. The result is a lower ability of the breaker to reject heat to its environment. That means that if you run the full rated current through the breaker, the steady-state temperature of the thermal trip unit will be higher than previously; the equilibrium has shifted. That temperature may now be above the trip point, causing the breaker to trip when you don't want it to.
A work-around for this is to prohibit continuously running the full rated current through the breaker. Somehow the factor of 80% was arrived at, it was judged that reducing the current to at most 80% of the rating would shift the equilibrium temperature back sufficiently to avoid unintended tripping. In other words, you need to oversize the breaker by a factor of 125%.
Code-wise, that factor of 125% requires upsizing the conductors by 125% as well; otherwise the conductors would be underprotected by the breaker. [And upsizing the conductors has the further benefit of improving the breaker's ability to reject heat via conduction through the conductors.] The code writers chose to put the requirements in terms of upsizing the conductors as the first matter, with the upsized breaker as a side effect. I don't find that particular enlightening, since the limitations of thermal trip units are the whole reason for the requirement, so I prefer to think of it as upsizing the breaker as the first matter, with the upsized conductors as a side effect.
Cheers, Wayne