Our facility has been experiencing this problem for several years. It is very intermittent and doesn't happen very often, maybe 4 times a year on average. Often enough to be very annoying to a production plant.
We get what seems to be a very brief phase loss that causes several minor production problems across the shop. It seems like it is different phases based on different equipment shutting down. Lights may flicker, chillers may drop out, compressors may shut off, other various production equipment & machines may shut down or alarm out, but they seem to be grouped as if A, B, or C is feeding the control power to different things.
We have looked at our service equipment several times never seeing anything of concern. Most recently it was both buildings that experienced the glitch, proving that it was POCO related (proving this time at least) as each building if fed from separate utility lines. Another reason to suspect POCO is that machines fed from separate services inside the building, but the same utility lines, are affected the same during each occurrence. And again, being that it is randomly different phases makes me think it is POCO related.
There is a large substation just up the road and I think it may be related to them switching things or some other such thing. Maybe?
Anyway, how should I go about investigating this? Its not a big emergency but we want to look into it. Should I call POCO (ComEd) and explain the issue?
How about inside our building? I plan to check tightness of the incoming lines during the next shutdown, and thought about using an IR thermometer to check temps in the mean time.
We get what seems to be a very brief phase loss that causes several minor production problems across the shop. It seems like it is different phases based on different equipment shutting down. Lights may flicker, chillers may drop out, compressors may shut off, other various production equipment & machines may shut down or alarm out, but they seem to be grouped as if A, B, or C is feeding the control power to different things.
We have looked at our service equipment several times never seeing anything of concern. Most recently it was both buildings that experienced the glitch, proving that it was POCO related (proving this time at least) as each building if fed from separate utility lines. Another reason to suspect POCO is that machines fed from separate services inside the building, but the same utility lines, are affected the same during each occurrence. And again, being that it is randomly different phases makes me think it is POCO related.
There is a large substation just up the road and I think it may be related to them switching things or some other such thing. Maybe?
Anyway, how should I go about investigating this? Its not a big emergency but we want to look into it. Should I call POCO (ComEd) and explain the issue?
How about inside our building? I plan to check tightness of the incoming lines during the next shutdown, and thought about using an IR thermometer to check temps in the mean time.