I have a panel on a rooftop. Circuit in question has a 35 amp breaker, #8's (XHHW-2).
Two scenarios:
1. A breaker in the panel is supplying a roof top unit with a MCA of 35 and MOP of 50. The circuit breaker in the panel serves as the disconnect and over current protection for the equipment. So I can use #8's.
2. Now, same as above but I add a fusible disconnect between the panel and unit fused at 50 amps with #8's running between the disconnect and the RTU. Now the wires between the panel and disconnect need to be #6. Is this correct?
Practically I don't see a difference between the 2 situations but code wise it seems like there is a difference because the conductors supplying the disconnect become a feeder as opposed to a branch circuit?
Thoughts?