Hey everyone,
I need some opinions. I am installing two dedicated 120V 20A single phase circuits that will terminate at two quadplex outlets in an information technology environment that will power some Networking equipment. My concern is this. The two outlets will be located 200 feet away from the panel I have to come out of and I am worried about voltage drop. I understand that the NEC only recommends a 3% voltage drop limit on branch circuits. I do not know the exact load that will be on these circuits because these circuits will be providing power for a Networking test area so the load will vary from day to day. Using the VD formula
2 x K x I x D divided by CM, I use the following
numbers.
K = 12.9
I = 16A ( I am using this figure because I don't know what the load will be and 210.21(B) (2) tells me that "where connected to a branch circuit supplying two or more receptacles or outlets, a receptacle shall not supply a total cord-and-plug-connected load in excess of the maximum specified in Table 210.21 (B) (2) )
D= 200 feet
CM= 6530 (From table 8)
Plugging these numbers into the above formula I get a voltage drop of 12.64V, that is 10%. When should I start being concerned about voltage drop?
Thanks for your comments,
Kevin
I need some opinions. I am installing two dedicated 120V 20A single phase circuits that will terminate at two quadplex outlets in an information technology environment that will power some Networking equipment. My concern is this. The two outlets will be located 200 feet away from the panel I have to come out of and I am worried about voltage drop. I understand that the NEC only recommends a 3% voltage drop limit on branch circuits. I do not know the exact load that will be on these circuits because these circuits will be providing power for a Networking test area so the load will vary from day to day. Using the VD formula
2 x K x I x D divided by CM, I use the following
numbers.
K = 12.9
I = 16A ( I am using this figure because I don't know what the load will be and 210.21(B) (2) tells me that "where connected to a branch circuit supplying two or more receptacles or outlets, a receptacle shall not supply a total cord-and-plug-connected load in excess of the maximum specified in Table 210.21 (B) (2) )
D= 200 feet
CM= 6530 (From table 8)
Plugging these numbers into the above formula I get a voltage drop of 12.64V, that is 10%. When should I start being concerned about voltage drop?
Thanks for your comments,
Kevin