If I know the available fault current (AFC) at a 480/277V panel, and I power a 480V delta to 208/120V transformer from it, what is the effect of the transformer on AFC at 208/120V?
I have an electrical drawing for the building that shows the AFC for the 480V panel and for a similar transformer fed from it. It shows the AFC for a panel connected to the secondary of the stepdown transformer as less than 1/3 of the AFC at the 480V panel; and I am trying to make sense of it. I am guessing that this is due to the %Z of the stepdown transformer; am I on the right track?
I have an electrical drawing for the building that shows the AFC for the 480V panel and for a similar transformer fed from it. It shows the AFC for a panel connected to the secondary of the stepdown transformer as less than 1/3 of the AFC at the 480V panel; and I am trying to make sense of it. I am guessing that this is due to the %Z of the stepdown transformer; am I on the right track?