Working on a new municpal office building, 5 stories, 60,000SF. It will have a generator for selected areas identified to be fully operational, as well as the data center, elevators, etc. I also will be using the generator for emergency lighting throughout the entire building. The building is 277/480V.
With a bunch of different departments, each having several hallways, conference rooms, bathrooms, breakroom, etc. My first choice is have the designated emergency fixtures wired unswitched as nightlights......I have the extra capacity in the generator so load is not a problem....This approach would be sort of wasteful, but for a $100 GTD type device per fixture, there would never be a payback on not operating one or two less lamps. I could also only wire one ballast of a two lamp fixture as a nightlight as a less expensive approach.
I will probably add a central lighting control panel to control the public and hallway lighting, lighitng in the cube farms, bathrooms, breakroom, etc. so I guess I could control it this way. The lighting control panel would sense the generator running and force these lights on. All other individual offices would have occ. sensors.
How do others design\install the lighting control of the emergency lights for multiple rooms.