I have some 200 HP motors at 480V, so from the table that is 240 A.
240X1.25 = 300.
The least amount of copper I can use is (2) 1/0, or I can use a single 350 KCM.
One 350 KCM conductor is about 1.65 X as much copper as two 1/0 conductors.
I have a 400A CB on the motors, so a #3 EGC.
Do I have to upsize the #3 by 1.65X if I use a single 350 instead of (2) 1/0? That would put me into a 1/0 for the EGC which would normally be adequate for an 800A CB.
Really, they need to revise this section of the code.
240X1.25 = 300.
The least amount of copper I can use is (2) 1/0, or I can use a single 350 KCM.
One 350 KCM conductor is about 1.65 X as much copper as two 1/0 conductors.
I have a 400A CB on the motors, so a #3 EGC.
Do I have to upsize the #3 by 1.65X if I use a single 350 instead of (2) 1/0? That would put me into a 1/0 for the EGC which would normally be adequate for an 800A CB.
Really, they need to revise this section of the code.