More quality work,

Status
Not open for further replies.

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
How many violations can you find?
On top of what you see, the neutrals and grounds were on the wrong bussbars in the new panel.
 

Attachments

  • F8EC52F2-4A62-4D1F-895C-A1A67D34EF60.jpeg
    F8EC52F2-4A62-4D1F-895C-A1A67D34EF60.jpeg
    991.1 KB · Views: 114

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The individual conductors, obviously, and the conduit in the bottom of the old box has almost broken out the concentric KOs.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
The individual conductors, obviously, and the conduit in the bottom of the old box has almost broken out the concentric KOs.
What do you mean the KO, the whole bottom has been caved in (pushed up).
When did they start allowing THHN to be run without a wireway?
 

jap

Senior Member
Occupation
Electrician
What do you mean the KO, the whole bottom has been caved in (pushed up).
When did they start allowing THHN to be run without a wireway?


Isn't this exactly what Larry said? :)

Ok,,, I'll add to it.,, doubled up conductors under the lugs,,,

JAP>
 

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
They also have the copper in the terminals with the aluminum to tap the feeder.
 