Thanks Bobiwire said:These become very practical when you need more meters than 4 or 5 in one location.
Dennis Alwon said:Thanks Bob
We call them meter banks.
jaylectricity said:Looking at those meter banks IWire posted it reminds me of a problem I'm about to have. I'm going to need 7 meters with one of them being a meter bypass socket. Can I get a 6 gang meter socket for outdoor use? The electric company wants them outside as they are currently in the basement. I have to replace 6 fuse panels with circuit breaker panels for apartments in the building, plus I need to add a 100 amp service to take care of the common areas plus we are adding a small laundry area.
Do I need to put 100 amp panels for each apartment? It seems excessive. They are currently fused by 60 amp mains for each apt. but I know that 100 amps is the minimum service allowed by law I just don't know if it still matters since the main service drop will be rated for 200 amps.
Will I need an outdoor main disconnect for the whole building?
I'm trying to put together a price but I don't have much experience in doing multi-meter services. Any help piecing this together would help me figure out what I need to do
Thanks,
Jay
Most of these style are outdoor rated, at least the cutler hammer stuff is. I would be the seimans is as well. The sockets will be rated @ 100A but you should be able to use 60A Breaker/Feeder in a Multifamily dwelling(230.79 (D)). The Bypass on this style is usually seperate from the "stack", unless you ned bypass on all.
Tom
iwire said:The above picture is not what we call a meter bank in this area.
Here are what we would call meter banks.
or a newer one with an added lever bypass.
Modular meter centers will often have 10, 20, 30, 40 meters 5 rows high by 6 ,8, 10 columns wide.
They also have main breakers for each unit and a Main service disconnect all connected with out any field wiring.
Here is a small but better picture of a Meter Center, you can see the bus bars sticking out for the next section.
iwire said:Here is a section of a Modular meter center.
We are looking at the top side of a vertical section
These become very practical when you need more meters than 4 or 5 in one location.
You hang a matching fused switch or breaker enclosure as the service disconnect, than you buy as many sections as you need. Each section may have 2 to 6 meter spots. All these vertical sections bolt together quickly including the connecting bus bars.
Typically the service is 208Y/120 with single phase meter sockets.
Now all that said I have never seen these modular meter centers above 200 amps per socket.