I am curious as to whether I should apply Table 310.15(B)(3)(a) to the load on a feeder for a bussed gutter system. I have 2 sets of (4)#350 and the bussed gutter is estimated at a demand load of 560A for a 600A service. The calculations for the demand load on the individual panels on this service were done per NEC. The continuous loads were calculated at 1.25, the non-continuous loads were calculated at 1.00, etc.
With that table, I would cap the full calculated demand load at about 488A (80%), correct? Do I assume that all 4 feeders are carrying current, including the neutral because it is most likely a non-linear load?
Thank you