OK, so I'm freaking out a bit here. Three years ago when I redid my backyard and put in a pool I put a 2" PVC conduit in from my main electrical panel about 120' to an area of my lot I'd like to eventually build a guest-house. (thinking ahead!) It basically goes underground, winds around a bit and ends up roughly in the middle of where I thought the pad would be.
So now we're getting to the build of the guest house and it occurs to me that I've already got 330 degrees of bends in the route and I'm likely to need another 45 and then a sweep up to my electrical panel. That's 330+45+90=465 degrees! (FWIW, the conduit currently still terminates underground at 330 degrees. I still have to uncover the end and run the extra 90+45).
So I'm freaking out that all my forethought is for not. I put in a full 2" PVC even though I'm only running 125 A just in case.
Am I'm screwed here? Should I buy #1 copper instead of #2/0 Al just to make sure things can run. Will that even work? What should I do?
So now we're getting to the build of the guest house and it occurs to me that I've already got 330 degrees of bends in the route and I'm likely to need another 45 and then a sweep up to my electrical panel. That's 330+45+90=465 degrees! (FWIW, the conduit currently still terminates underground at 330 degrees. I still have to uncover the end and run the extra 90+45).