2008 NEC allows panels with more than 42 circuits. Are they now available?
2008 NEC allows panels with more than 42 circuits. Are they now available?
If you are only using top or bottom Ko's you definately need to use more than two poles per KO. not easy to do with NM cable or MC cable. With raceways it is probably not much a problem as long as you use at least 3-6 poles per raceway.Square D has panelboards available up to 84 circuits, I believe. I don't think too much of them, as I am not sure there is enough space to bring in that many conduits, especially with 1 neutral to every "hot". I would still use double tubs for most applications, unless maybe they are filled with smaller 3 phase loads.
Bob
If you are only using top or bottom Ko's you definately need to use more than two poles per KO. not easy to do with NM cable or MC cable. With raceways it is probably not much a problem as long as you use at least 3-6 poles per raceway.
A 1933 panelboard fire that had all the flammable insulation, cloth covered rubber.Yes, just seen a 60 circuit installed here lately. I wonder what lead up to the 42 max in panels in the first place.
A 1933 panelboard fire that had all the flammable insulation, cloth covered rubber.
double barrel connector, 12/4 mc 6 poles per ko
Yes, 2 extra neutral bars, as well as 2 ground bars. And, a grounding lug at the top (did you catch that?)