I have a new house with a single phase service. I have an automatic transfer switch for my generator. The 200 amp breaker at the auto transfer switch is used as an emergency disconnect and a service disconnect.
There are 2 legs and a neutral from the meter trough that are brought into the auto transfer switch which has an integral 200 amp breaker on the normal supply. The generator connection has 4 conductors, L1 and L2 connected to the transfer switch, a neutral connected to the neutral bus in the ATS and a ground connected to a ground bus in the ATS (this ground is only a chassis ground for the generator). The neutral bus and ground bus are bonded here.
There are only 3 conductors from the ATS cabinet to the breaker panel in the house (about 140 feet away), L1, L2 and a neutral. There is no ground conductor.
There is no main breaker at the panel. At the panel there is a ground conductor run outside to 2 ground rods and the neutral bus is bonded to the ground bus in the panel via a bonding screw.
Questions:
What is the better method of connection, what I have or consider the ATS to be service entrance and have the ground derived there (add ground rod(s)) and consider the panel in the house a sub panel?
In that arrangement, I know I need a ground conductor (minimum #6) run to the panel with the high sides and the neutral and then separate the neutral and the ground in the panel.
If this is better, is it best to abandon the existing ground rods. I don't think I want to be the best ground in the neighborhood.
I will be adding a tap off the existing line (10 foot rule) for a shed. While scoping that out I realized there was no ground from the cabinet where the main breaker is to the breaker panel. This got me wondering.
There are 2 legs and a neutral from the meter trough that are brought into the auto transfer switch which has an integral 200 amp breaker on the normal supply. The generator connection has 4 conductors, L1 and L2 connected to the transfer switch, a neutral connected to the neutral bus in the ATS and a ground connected to a ground bus in the ATS (this ground is only a chassis ground for the generator). The neutral bus and ground bus are bonded here.
There are only 3 conductors from the ATS cabinet to the breaker panel in the house (about 140 feet away), L1, L2 and a neutral. There is no ground conductor.
There is no main breaker at the panel. At the panel there is a ground conductor run outside to 2 ground rods and the neutral bus is bonded to the ground bus in the panel via a bonding screw.
Questions:
What is the better method of connection, what I have or consider the ATS to be service entrance and have the ground derived there (add ground rod(s)) and consider the panel in the house a sub panel?
In that arrangement, I know I need a ground conductor (minimum #6) run to the panel with the high sides and the neutral and then separate the neutral and the ground in the panel.
If this is better, is it best to abandon the existing ground rods. I don't think I want to be the best ground in the neighborhood.
I will be adding a tap off the existing line (10 foot rule) for a shed. While scoping that out I realized there was no ground from the cabinet where the main breaker is to the breaker panel. This got me wondering.