When setting motor overloads, is it 125% of full load amps?
When setting motor overloads, is it 125% of full load amps?
I can't find anything about rating overload protection for a moror in those articles.........
Maybe I have a different book................. :huh:
I'll keep looking..
(just playing, have a great one)
III. Motor and Branch-Circuit Overload Protection
430.32 Continuous-Duty Motors.
(A) More Than 1 Horsepower. Each motor used in a
continuous duty application and rated more than 1 hp
shall be protected against overload by one of the means
in 430.32(A)(1) through (A)(4).
(1) Separate Overload Device. A separate overload device
that is responsive to motor current. This device shall be selected
to trip or shall be rated at no more than the following
percent of the motor nameplate full-load current rating:
You absolutely MUST read the manufacturers instructions on setting the OL relay or selecting the heater elements (as the case may be). Some manufacturers tell YOU to factor in the 125%, some tell you they have ALREADY factored that in, and you MUST set/select based on the motor nameplate FLC. If you have one that is ALREADY factoring in that 125% pickup point, and you do it AGAIN, you will lose your motor if there is an overload.It really is found in 430.32 as another poster pointed out, and not 430.92 as I said. Weird typo.
You absolutely MUST read the manufacturers instructions on setting the OL relay ....