most accurate voltage drop formula

Status
Not open for further replies.

Hameedulla-Ekhlas

Senior Member
Location
AFG
VD = (1.732*I(RcosO + XsinO)*l*100/(380*1000)

R = Resistance per km per phase
X = Reactance per km per phase
I = Ampere or current
l = length in meter
100 = is because of percentage
1000 = to convert length from km to meter
380 = is line to line voltage
 

Hameedulla-Ekhlas

Senior Member
Location
AFG
The above formula is the standard formula for voltage drop. If you need more formula about the voltage drop and in different condition they are used please see the attached file.
 
Status
Not open for further replies.
Top