Motel end tables

Status
Not open for further replies.

boatfull

Member
In a motel, they have put new end tables next to the beds. They installed a UL receptacle strip on the cabinet. The receptacle is manufactured by www.furnlite.com model fc-739. The pigtail is 14-3 and the branch circuit supplying the rooms are 20 amps. The way I see it they are extending the branch circuit to the end table. I told the GC they have to put a 12-3 pigtail on the approved strip. Any thoughts?
 
I don't see it as any different than plugging in any other listed device in with 14-2(or 3). There are a ton of things made/listed with #14 conductors that plug into 20A circuits. IMO, you would be violating the listing by changing the pigtail to #12. It's just a convenience outlet and probably won't even see close to 15A much less 20A.
 
IMO unless the strip requires that it only be used on a 15 amp circuit it's not an issue.
 
When you said pigtail I went looking for a couple of #14 conductors thinking that it gets mounted to an electrical box. That's a LINE CORD and no, being #14 with a 15A plug does not extend the 20A circuit any more than plugging a lamp in. It's just another power strip.

-Hal
 
Seems to me that the receptacle the strip plugs in to is a glorified JB for the strip- i/e 12g attached to 14g. Does 240.5 point to needing a 12 ga pigtail? I dont think I'd want a 14g power strip snaking along the floor (say) in my house protected by a 20 a ckt.
 
Seems to me that the receptacle the strip plugs in to is a glorified JB for the strip- i/e 12g attached to 14g. Does 240.5 point to needing a 12 ga pigtail? I dont think I'd want a 14g power strip snaking along the floor (say) in my house protected by a 20 a ckt.
That is very arbitrary. Christmas tree light strings are often 20 gauge wire fed by an extension cord with 18 gauge wire strung across the floor.
 
Seems to me that the receptacle the strip plugs in to is a glorified JB for the strip- i/e 12g attached to 14g. Does 240.5 point to needing a 12 ga pigtail? I dont think I'd want a 14g power strip snaking along the floor (say) in my house protected by a 20 a ckt.

Better unplug your fridge. I seriously doubt the cordset has a 12/2 cable. 1500 watt hairdryers don't have 14 AWG cords. All normal and safe if listed.
 
It looks to me like the code is making a distinction between flexible cord and fixture wire/lamp cord wire. The strip feeds utilization equipment whereas christmas lights are utilization equipment.
 
It looks to me like the code is making a distinction between flexible cord and fixture wire/lamp cord wire. The strip feeds utilization equipment whereas christmas lights are utilization equipment.

And this https://www.amazon.com/dp/B00178HJ6C/ref=psdc_495312_t1_B0775W1GRX is a 16 gauge extension cord 12 feet long that is commonly used to feed that utilization equipment. Perhaps you missed that part of my description.

don't make a mountain out of a molehill.
 