are arc fault breakers required for motel rooms. As in residential homes.

210.12 specifies Branch Circuit AFCI protection in dwelling units. Should motel suites meet the definition of a dwelling unit having independent living facilities, then yes. rbj
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Does the motel room qualify as a dwelling unit?

Take a look at 210.18

210.18 Guest Rooms and Guest Suites.
Guest rooms and guest suites that are provided with permanent provisions for cooking shall have branch circuits installed to meet the rules for dwelling units.

Chris
 

ronball

Senior Member
Location
Champaign Il.
Occupation
Electric Contractor
arc fault breakers

arc fault breakers

Thanks for your response. motel rooms do not include any cooking facilities,etc. just beds and bathrooms. inspector was to get back with me, but he didn't. ronball
 

luckyshadow

Senior Member
Location
Maryland
Do you think sprinkler systems lift the requirement for afci's in motel rooms?

Why would they?
They are putting sprinklers in houses and you are required to use AFCI.

Sprinklers are designed to extinguish a fire.
AFCI are designed to prevent a fire from starting.
 