Motor amp calculations
HP is a mechanical value, not electrical. To get (single phase) Amps from HP, it is Watts / Volts x PF x Eff. Also, for the NAMEPLATE values, make sure you read the NAMEPLATE volts. For 120V, it is usually 115V on the nameplate. So for a 2HP motor, it is 1492 / 115 x .7PF x .8Eff = 23.16A. a lot closer to the NEC tables. The NEC tables are based on "industry typical" 4 pole motors, decidedly slanted to be able to cover the worst case, and, because the tables go a long way back before energy efficiency was a thing, the values are higher than we see on motors today. They are based on roughly 1970s motor technology (the oldest NEC I have is 1978, the chart is the same).