Good morning,
Just trying to get some clarity for a customer.
I have a 3 phase 40 amp motor for a compressor fed from a starter, the starter is fed from a 60 amp fused disconnect.
When the motor is running I have 40 amps/28amps/21amps on the load side of the disconnect. It seems as if the motor is not drawing enough amperage and the motor could be failing. Sometimes when the compressor is turned on the lights in the area get dimmed and the compressor wont start. Shut it off and turn it back on and it works fine again.
I noticed that the contacts are a little beat up and looking to get those cleaned up, the heaters themselves look fine but I did not remove to check behind them to see if there was any melting.
I am not too familiar with these types on installations and what could be the source of the problem so any info can help. I was going to order a contact kit and replace the internal parts of the starter, but if it is in fact the motor failing this will be for nothing. What is the correct way to see if the motor itself is failing?
Should I test voltage across each leg of the load side of the disconnect to make sure the proper voltage is there when motor is running? Also test voltage on starter when motor is running?
Any info would help.
Thank you!
Just trying to get some clarity for a customer.
I have a 3 phase 40 amp motor for a compressor fed from a starter, the starter is fed from a 60 amp fused disconnect.
When the motor is running I have 40 amps/28amps/21amps on the load side of the disconnect. It seems as if the motor is not drawing enough amperage and the motor could be failing. Sometimes when the compressor is turned on the lights in the area get dimmed and the compressor wont start. Shut it off and turn it back on and it works fine again.
I noticed that the contacts are a little beat up and looking to get those cleaned up, the heaters themselves look fine but I did not remove to check behind them to see if there was any melting.
I am not too familiar with these types on installations and what could be the source of the problem so any info can help. I was going to order a contact kit and replace the internal parts of the starter, but if it is in fact the motor failing this will be for nothing. What is the correct way to see if the motor itself is failing?
Should I test voltage across each leg of the load side of the disconnect to make sure the proper voltage is there when motor is running? Also test voltage on starter when motor is running?
Any info would help.
Thank you!