If you have a motor that the nameplate says 230V/115V and the amps say 7/14, would the fact that the actual voltage is 240/120 change the amp rating?
Seems if you do the math that the KW would be 1610 and using 230V, you get the nameplate rating.
But if you use 240V with the same KW, you get 6.7A/13.42A.
Is this the way it would work, or is the nameplate what I have to use?
I'm trying to figure if I can run two motors off of a 20A circuit. These motors are for a swimming pool and spa.
I assume (maybe wrong) that I need to factor in 125% for continuous use since it's possible that these will run for three or more hours at a time.
One is the motor mentioned above 230/115 - 7/14
The other is 230/115 - 9.7/19.4
I will run 240V on a 20A circuit if I can do this.
I just remembered that the 125% is probably already factored in the nameplate, is that correct?
Seems if you do the math that the KW would be 1610 and using 230V, you get the nameplate rating.
But if you use 240V with the same KW, you get 6.7A/13.42A.
Is this the way it would work, or is the nameplate what I have to use?
I'm trying to figure if I can run two motors off of a 20A circuit. These motors are for a swimming pool and spa.
I assume (maybe wrong) that I need to factor in 125% for continuous use since it's possible that these will run for three or more hours at a time.
One is the motor mentioned above 230/115 - 7/14
The other is 230/115 - 9.7/19.4
I will run 240V on a 20A circuit if I can do this.
I just remembered that the 125% is probably already factored in the nameplate, is that correct?