anybody can help giving advice how to eliminate or at least minimize motor bearing current during the motor is running ( in operation )??
Thnx,
Rgds
Thnx,
Rgds
anybody can help giving advice how to eliminate or at least minimize motor bearing current during the motor is running ( in operation )??
Thnx,
Rgds
We had somebody ask us about using ceramic bearings on the motors for their air handlers.I think the most effective solution is the grounding brushes on the motor shaft and changing the motor bearings to ceramic coated bearings so that they do not create a path between the armature and ground.
I have seen just grounding brushes put on the motor shafts but that can only divert some of the current from the bearing.
I think the most effective solution is the grounding brushes on the motor shaft and changing the motor bearings to ceramic coated bearings so that they do not create a path between the armature and ground.
I have seen just grounding brushes put on the motor shafts but that can only divert some of the current from the bearing.
I think the most effective solution is the grounding brushes on the motor shaft and changing the motor bearings to ceramic coated bearings so that they do not create a path between the armature and ground.
anybody can help giving advice how to eliminate or at least minimize motor bearing current during the motor is running ( in operation )??
Thnx,
Rgds
Anyone has eperience to install the grounding brush during the motor is running. This motor is very critical to the Plant. No chances to stop it. The plant turn arround schedule is still long.
anybody can help giving advice how to eliminate or at least minimize motor bearing current during the motor is running ( in operation )??
Thnx,
Rgds
It is somewhat puzzling that whereas this was a recognized problem with large motors, manufacturers report an increasing number of damage on smaller motors <50HP. Could it be the greatly increased use of drives, or is it carrier frequency related or perhaps drive end technological change?The jury is still out on this issue. On large machines, when you specify inverter service, manufacturer will supply insulated bearing on one end and some places a grounding brush-bushing on the opposite end.
Lastly, these can not be used in hazardous locations. Of course one asks what happens to the arcing within the bearing that is perhaps even higher energy discharge than the brushes would produce.:lol: The respective IEEE motor standard committees are still scratching their heads, so far, on this issue.
This is interesting, especially since the NEMA frame motors are mass produced in such large quantities to tolerances sufficient to meet .08 ips vibration (IEEE 841) or even .04 ips vibration (GE's IEEE 841 line). One would think that the magnetic asymmetry would be minimized by the automated manufacturing processes.....
Another one of the great mysteries - just like how we have T-ratings and maximum permissible surface temperatures on electrical equipment but a 600# steam line with a surface temperature above the AIT can run through the process area....