Motors have never been my best friends. One of my engineers asked this question, and I can’t answer it.
You have, in order, a circuit breaker within a branch panel, a cable, a fused disconnect, a cable, a motor controller, a cable, and an elevator motor. The controller is rated at 100 amps. The motor has a starting current of 236 amps and a full load current of 79 amps.
If I sized the breaker or the fuse to allow for the starting current, then neither would protect the controller at its rating. What ratings do I assign for the breaker, the cables, and the fuse?
Charlie -
There are already several good posts concerning the code issues - so I won't comment on that. Let's look at this from the point of what are we trying to protect and why. I am going to limit my discussion to normal industry motors/loads installations.
Disclaimer: You used the word "elevator'. I don't do elevators, so there may be elevator codes/Life Safety codes that I am not aware of.
First, the circuit loading is limited by design, not by the circuit breaker or fuse. The motor is selected such that it is operating within spec - normal circuit loading is fine.
Now one must protect the equipment and personnel in the event of a fault/malfunction. For this limited discussion, the controller always has an overload device. This is set to protect the conductors between the feeder CB to the motor - but not necessarily the motor. The overload trip curve is inside of the cable damage curve, but not necessarily inside of the motor damage curve. For example, a typical industrial installation is a combination starter, consisting of a mag-only CB, contactor, overload. I tend to set the overloads (1.15sf motor) to 140%, and mag only to the NEC max (generally 11x to 17x fla, depending on the motor). The overload curve has to be outside of the motor starting curve. The mag trip has to be outside of the inrush (which can be substantially greater than the nominal 6x fla.
Say the motor/mechanical load malfunctions - dragging bearings,stuck relief valve, binding coupling, internal motor electrical fault that does not result in a short circuit. The overloads will trip before the conductors are damaged. If the cause is a motor internal fault, there is no motor to save. It's toast. If it is a mechanical malfunction, again the overloads will trip saving the conductors. And one could get lucky and have a motor still worth rebuilding - but no guarantee on that.
Now if the motor or conductors between the overloads and motor, develops a serious fault, as in short circuit, there is no motor to save, or no conductors to save. So the starter CB/fuses are set to get the fire put out as quickly as possibe. One could say the CB/fuses are selected to protect the structure - and the personnel are protected by not having the structure catch fire.
One might say the conductors between the feeder CB and the overloads are not protected from overload. Well they are - any current going in the feeder CB end has to come out of the overload end. Anything else is a backhoe/forklift attack - again, there are no conductors left to protect, just a fire to put out to protect the structure.
enough with the philosophy
Your specific case:
TM CB in a panel
conductors to fused disconnect (in controller)
controller (with overloads in any of my applications)
Conductors to motor
Motor FLA 79A
This is not something I normally have to deal with - however, here is the method I would use (assuming a design B, code G motor):
Consider the panel TM CB is the 430.52 short circuit protection. Set it at 250% (unless it is a screwie motor). Conductors to controller are sized at 125%. The controller fused disconnect is there to provide the controller disconnect. Slug it if you want - the fuses serve no purpose. Or, use the exception and select the longest time delay fuses available at 225%. Set the overloads to max 140% for sf 1.15, 130% for sf 1.0. Conductors from controller to motor are 125%.
There is no reason to size the conductors from the panel to the controller larger than the motor circuit conductors (other than NEC legal wrangling). I would not expect an AHJ to complain. If they did, I'd suggest the controller fused disconnect was for the required in-sight controller disconnect and did not perform short circuit protection - the panel CB did that. If she drug her feet, I's suggest we could slug the fused disconnect. It the AHJ was still stuck, I'd replace the controller fused disconnect with a non-fused disconnect.
I know this reads somewhat scrambled - but I'm short on time. Susposed to be working a paying job. If someone see flaws in my reasoning - I'm interested. I'm not stuck.
The worm