Hi,
I have to select conductor size and OCPD for motor branch circuit. The motor is 20hp at 480V 3ph.
If I select 70A Short circuit/Ground Fault protection device based on 430.52, is #10 awg conductor still acceptable per NEC (it meets the min ampacity requirement for this motor FLC) ,or will it not meet the conductor overcurrent limitation per 240.4(D)?
I think the exception is 240.4 (G) allows me to proceed with my selection (#10 awg and 70A breaker) but hoping to get some opinion here. Thanks