Hi all,
I have a client who wants me to wire up some equipment for his wood shop (dust collection, compressor, etc.). I'm hoping that If I explain one scenario then I can apply it to the other equipment... None of the equipment has documentation on branch circuit/OCP. Only wiring configurations. I'm looking to get some input on my calcs and what the mfg. had in mind when they installed a 20A plugon one of these pieces of equipment.
Compressor (motor #1): 5 HP/230V = 28A FLC at 230V (per table 240.248) *125% = 35A
Branch circuit condutors = 40A @ 60'C = #8THHN
MOCP = 28A FLC * 250% (per table 430.52) = 70A
Can someone tell me why the manufacturer installed a 20A/250V plug (NEMA 6-20P) on the compressor? It would seem to me that this is way undersized for the branch circuit that I calculated.
Also, I know that the Max. OCP can be up to 250% of the motor's FLC. But should I necessarily size it that large? I know it is to protect the conductors...the overload protection is for the motor. Is there any reason to start at a lower OCPD and go up from there? I often hear of people (electricians - they are people, right?
) who talk of that, but I've never understood why.
I am running from a 110/220V panel upstairs with Inverse-time breakers and am going to install plug and cord disconnects for some of the equipment and non-fusible disconnects for others. Some of the dust collection equipment needs to be rolled away to make emptying the bins easier. Am I to understand the in each circumstance that the disconnects need to be rated at not less than 115% of the FLC (430.110 (A))?
I don't typically do this kind of work, but would like to know if I'm on track. No, I'm not a handyman - NC licensed, limited class.
I appreciated any and all input...
Scott
I have a client who wants me to wire up some equipment for his wood shop (dust collection, compressor, etc.). I'm hoping that If I explain one scenario then I can apply it to the other equipment... None of the equipment has documentation on branch circuit/OCP. Only wiring configurations. I'm looking to get some input on my calcs and what the mfg. had in mind when they installed a 20A plugon one of these pieces of equipment.
Compressor (motor #1): 5 HP/230V = 28A FLC at 230V (per table 240.248) *125% = 35A
Branch circuit condutors = 40A @ 60'C = #8THHN
MOCP = 28A FLC * 250% (per table 430.52) = 70A
Can someone tell me why the manufacturer installed a 20A/250V plug (NEMA 6-20P) on the compressor? It would seem to me that this is way undersized for the branch circuit that I calculated.
Also, I know that the Max. OCP can be up to 250% of the motor's FLC. But should I necessarily size it that large? I know it is to protect the conductors...the overload protection is for the motor. Is there any reason to start at a lower OCPD and go up from there? I often hear of people (electricians - they are people, right?
I am running from a 110/220V panel upstairs with Inverse-time breakers and am going to install plug and cord disconnects for some of the equipment and non-fusible disconnects for others. Some of the dust collection equipment needs to be rolled away to make emptying the bins easier. Am I to understand the in each circumstance that the disconnects need to be rated at not less than 115% of the FLC (430.110 (A))?
I don't typically do this kind of work, but would like to know if I'm on track. No, I'm not a handyman - NC licensed, limited class.
I appreciated any and all input...
Scott