Motor Branch Circuit
joe1772
Virginia
I'm confused about conductor and fuse sizing of motor circuits.
Could some one please tell me the proper fuse size and conductor size for the following motors.
3 phase
208 V
squirrel cage motors
5 hp RLA=16.7
50 hp RLA=143
Also could you tell me if Article 240.4(D) applies to conductors suppling motors.
bphgravity
Florida
Re: Motor Branch Circuit
The F.L.C. of each motor is found at 430.148 for single phase and 430.150 for 3-phase.
Overload protection is sized per 430.32(A)(1) or 430.32(C).
Branch-circuit conductor size per 430.22.
Branch-circuit OCD per 430.52.
Feeder conductor (if motors are sharinga feeder) is sized per 430.24.
Feeder OCD is sized per 430.62.
240.4(D) does not apply to motor circuits, see part (G).
joe1772
Virginia
Thanks for the reply.
So the overloads, at 115%, should be 19.2A and 164.5A.
Time-delay fuses, 25A And 250A
Conductor sizes, THHN copper, 14 and 2/0
bphgravity
Florida
Look pretty good.
The first could be a 30-amp fuse: 16.7 x 175% = 29.2-amps. 240.4(B) allows you to go to the next stabdard size. If the motors trip the OCD on the start, 430.52(C)(EX. 2)(b) allows the percentage be increased to a maximum of 225% of the FLC.
#12 and 3/0 would most likely be needed. Even though you are using THHN 90 degree conductors, they can only be loaded to the 75 degree column.