We've got a discussion going about motor branch circuits. One guy maintains that #12 wire can never be used on a breaker over 20 amps, therefore the feeder for a 1 HP 115V motor must be #10, as this motor requires at least a 30A circuit breaker. Same issue for, say, a 15HP 460V 3 phase motor - it uses a 40A circuit breaker so a #10 would not be allowed.
THe other guy maintains that a motor branch feeder only needs to be 125% of the FLA, and the branch circuit breaker is irrelevant to the sizing of the wire. This would result in a 1HP 115V motor, with a 16 amp FLA, would be fine on a #12 wire.
Who is correct?
THe other guy maintains that a motor branch feeder only needs to be 125% of the FLA, and the branch circuit breaker is irrelevant to the sizing of the wire. This would result in a 1HP 115V motor, with a 16 amp FLA, would be fine on a #12 wire.
Who is correct?