Re: motor branch circuts
Don,
Actually, no. The Sq D chart is not for the dual listing.
So, I checked my Littlefuse chart and it shows the same info as your Bussman (with fuse reducers of coarse).
Also, the 60amp listing is for a motor with a service factor of <1.15 according to Littlefuse.
With a SF of >1.15, they list a 70amp.
Todd