motor branch ckts

Status
Not open for further replies.

donmore

Member
when sizing branch ckts for motors, do you use the ampacities for 14,12,10 awg wire listed on 310.16, or do you follow 240.4(d) for small conductors. please list code ref.
 
Re: motor branch ckts

You are permitted to use the 310.16 values. Table 240.4(G),motor and motor control circuit conductors.
 