D donmore Member Sep 14, 2004 #1 when sizing branch ckts for motors, do you use the ampacities for 14,12,10 awg wire listed on 310.16, or do you follow 240.4(d) for small conductors. please list code ref.
when sizing branch ckts for motors, do you use the ampacities for 14,12,10 awg wire listed on 310.16, or do you follow 240.4(d) for small conductors. please list code ref.
electricman2 Senior Member Location North Carolina Occupation Retired Electrical Contractor Sep 14, 2004 #2 Re: motor branch ckts You are permitted to use the 310.16 values. Table 240.4(G),motor and motor control circuit conductors.