Guy wants to install a fixed compressor on a dedicated circuit, but with a cord and plug/receptacle. Unit's instructions say to permanently wire, but he wants it "pluggable" so he can move it if necessary. For now, neglect the "not in accordance with the instructions" ...
430 calls out sizing for conductors and CB, and states a HP rated receptacle must be used. I contend that is what should be done.
Others have suggested that the motor sizing rules don't apply if you put a plug/receptacle on the branch, and you must size the wires/CB to the receptacle.
I can find no references to anything that indicates you can't size per 430 if you use a plug/receptacle.
Best answer, because of future homeowners, is probably to pick a receptacle to handle the motor, then size it all as a general purpose circuit?
430 calls out sizing for conductors and CB, and states a HP rated receptacle must be used. I contend that is what should be done.
Others have suggested that the motor sizing rules don't apply if you put a plug/receptacle on the branch, and you must size the wires/CB to the receptacle.
I can find no references to anything that indicates you can't size per 430 if you use a plug/receptacle.
Best answer, because of future homeowners, is probably to pick a receptacle to handle the motor, then size it all as a general purpose circuit?