motor breaker size protection

Status
Not open for further replies.

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
I have a dust collection system that I am connecting. It has a 3 phase 7.5 HP motor connected at 208 volt. cont. duty, des B, max amb C 40, nema nom EFF 89.5, the FLA is 21amp we have a Sq D qob panel feeding into a fused disconnect 30a time delay fuses, then to a stop start contactor. My quetion is what is the max breaker size I can put on this from the panel? at start up the motor jumps to 106 amps then starts to come down as speed builds up. Sq D has to fast of a trip setting to hold at 30amps. Thanks in advance motors are not my strong point.
 
acrwc10 said:
I have a dust collection system that I am connecting. It has a 3 phase 7.5 HP motor connected at 208 volt. cont. duty, des B, max amb C 40, nema nom EFF 89.5, the FLA is 21amp we have a Sq D qob panel feeding into a fused disconnect 30a time delay fuses, then to a stop start contactor. My quetion is what is the max breaker size I can put on this from the panel? at start up the motor jumps to 106 amps then starts to come down as speed builds up. Sq D has to fast of a trip setting to hold at 30amps. Thanks in advance motors are not my strong point.

First, you could use a Square D type QO330HID breaker which does not include the fast trip feature.

Second, you can only put in as large a breaker as what your wire is sized for. This breaker is for branch circuit protection (your fused switch provides the motor protection) so you can not use any of the "motor upsizing OCPD" options.
 
Thanks for the clarification Jim on the ocp. The branch circuit feeder can be anything I need because it is right next to the panel, connected with an offset nipple. What size would you think I should use to feed the fused disconnect with so as not to have a trip problem on the breaker?
 
jim dungar said:
First, you could use a Square D type QO330HID breaker which does not include the fast trip feature.

Second, you can only put in as large a breaker as what your wire is sized for. This breaker is for branch circuit protection (your fused switch provides the motor protection) so you can not use any of the "motor up-sizing OCPD" options.


Since I am going from the distribution panel to a fused disconnect wouldn't 430.52 allow me to up-size the breaker in the panel to 84 amp then to the next standard size 90 amp ( FLA is 21amp ) This give me ground fault protection for the conductors. The fuses in the disconnect after the panel are 30 amp time delay, which would protect the motor and conductors against over heating.
Edit to add -all conductors are #10 thhn
 
I wanted to say that you couldn't use the motor rules for the sizing and protection of the conductors between the panel and the disconnect, but the code doesn't say that. 430.62 permits a motor feeder to serve a single motor and be protected per Table 430.52. In this application the conductors between the panel and the disconnect are feeder conductors and the ones between the disconnect and the motor are branch circuit conductors.
It apprears that you can use #10 between the panel and the disconnect, but the maximum permitted OCPD is 250% of the FLA from Table 430.250. That would make the maximum size of the breaker in the panel 70 amps. (250% of 22.4 amps rounded up to the next standard size)
 
don_resqcapt19 said:
I wanted to say that you couldn't use the motor rules for the sizing and protection of the conductors between the panel and the disconnect, but the code doesn't say that. 430.62 permits a motor feeder to serve a single motor and be protected per Table 430.52. In this application the conductors between the panel and the disconnect are feeder conductors and the ones between the disconnect and the motor are branch circuit conductors.
It apprears that you can use #10 between the panel and the disconnect, but the maximum permitted OCPD is 250% of the FLA from Table 430.250. That would make the maximum size of the breaker in the panel 70 amps. (250% of 22.4 amps rounded up to the next standard size)

I feel better now, Thank you for confirming that table 430.52 was o.k. to use in this situation. It is suprizing to me that a motor that has a 16 amp ,normal load, jumps up to over 105 amps at start up.
 
acrwc10 said:
I feel better now, Thank you for confirming that table 430.52 was o.k. to use in this situation. It is suprizing to me that a motor that has a 16 amp ,normal load, jumps up to over 105 amps at start up.

8x inrush is not uncommon. Motor overloads relays are designed at 6x for either 10, 20, or 30 sec.
 
QES said:
why not use MCP breaker with upsteam overload?


We have to use the parts supplied to us. That means fused disco with stop start contactor. No MCP
 