kyle wattmeister
Member
I have a problem here. We have 2 motors on a cooling tower both pull 36 amps. we sized the wire by taking 36 x 1.25 + the sum of the other motor and we got 81 amps so we used # 4 wire. then we sized the breaker by taking 36 x 2.50 plus the sum of the other motor and we got 126 amps. so we used a 150 amp breaker. the inspector said that the wire was to small for the breaker and that we needed to put a 90 amp breaker in place of the 150 amp breaker. we tried to tell him that it would not hold the inrush of the two motors but he refused to reason with us. so we had to install the 90 amp breaker. which led us to the problem we are having now, the breaker keeps on tripping. the inspector called us back over to the job and said that it is the wire size that it is making it trip, so he had us install # 2 wire in place of the # 4 because of the derating of the ambient temperature. we tried to tell him that it was not going to work still because of the improperly sized breaker. he refused to listen to us. now the breaker is still tripping and he is now saying that he thinks the wires have a direct short. so we have to go back over there and meg them out.
can anybody tell me if im missing something
thanks in advance
kyle
can anybody tell me if im missing something
thanks in advance
kyle