bdrwirenut
Member
If I do a motor calculation for a 50 hp motor @ 460 volt the branch circuit overcurrent protection device is calculated by flc 65a times 250 %= 162.5a which would be a 175a standard breaker size correct? If you use the square d slide chart for motors they call for a 100a breaker for this motor where do they get the amp rating from. This question has come to my attention because several local panel builders use the 100a rating in their lift station control panels and I was wondering where the calculation came from.The same panel builders seem to apply step #6 of the motor calculation to the feeder breaker size but use the slide chart breaker size for the branch circuit breaker instead of step #4 could someone please explain this to me? Thank you for any help with this.