A megger is the best but a lot, most, of the time all it takes is your nose.
Here are a few basic steps (assuming a AC induction Motor)
(1) check each lead to ground---- all should read open or infinit resistance
(2) depending on the type of motor (3 phase) The leads come in pairs or wound poles,( I would have to look in a book to tell which are which) there shoud be some resistance ,but not a direct short . The last motor I did was about 8ohms in each.
(3) there should not be any continuity between adjacent/other poles.
When all basic test are complete
(1) wire it up like the namplates sez
(2) flip on the breaker and see if she blows up
(3) basic troubleshooting is complete
(4) if she runs , then run her till she blows (lets all of the magic smoke out)
(5) if she blows , get a new motor and try again..
there is a youtube on HOW ITS MADE large electric motors.
Really, thats how you T/S motors, just see if they blow up??
-Check bolted connection using a microhmeter
-Perform Insulation Resiatance test using a Megger, values depend on the motor type, size, and vintage
-Perform phase to phase stator wingin resistance tests using a winding resistance set
-Perform IR test on insulated bearings
These are for small LV motors, there are a few more tests for larger MV motors and other tests for something other than AC induction.
What would your total charge be to check out a typical 3/4hp 3ph 480v motor using your method?
Sold. I've got one you can sub out now. It's 25 miles away 30 foot up and forget the safety rail.:grin: Dress warm.
Just so I am clear - this does not include the drive out, the drive back and the report typed up and delivered?Well you would test it as part of a testing job, a motor like you described should take about 15 minutes to test, so about $20.