Motor burnt?
phatski
New member
I am fairly new to this so maybe you guys can help. How do you test a motor with a multimeter, to see if it is burnt ? I have a Fluke 87-5 multimeter that I will use. Thanks in advance. - Jeff
flip on the breaker to see it if blows up!!!
Here are a few basic steps (assuming a AC induction Motor)
(1) check each lead to ground---- all should read open or infinit resistance
(2) depending on the type of motor (3 phase) The leads come in pairs or wound poles,( I would have to look in a book to tell which are which) there shoud be some resistance ,but not a direct short . The last motor I did was about 8ohms in each.
(3) there should not be any continuity between adjacent/other poles.
When all basic test are complete
(1) wire it up like the namplates sez
(2) flip on the breaker and see if she blows up
(3) basic troubleshooting is complete
(4) if she runs , then run her till she blows (lets all of the magic smoke out)
(5) if she blows , get a new motor and try again..
there is a youtube on HOW ITS MADE large electric motors.
Really, thats how you T/S motors, just see if they blow up??
-Check bolted connection using a microhmeter
-Perform Insulation Resiatance test using a Megger, values depend on the motor type, size, and vintage
-Perform phase to phase stator wingin resistance tests using a winding resistance set
-Perform IR test on insulated bearings
These are for small LV motors, there are a few more tests for larger MV motors and other tests for something other than AC induction.
What would your total charge be to check out a typical 3/4hp 3ph 480v motor using your method?
Just so I am clear - this does not include the drive out, the drive back and the report typed up and delivered?
cf
Like I said, part of a testing job so there would be multiple motors. Obviously you want one little 3/4 hp motor tested either do it yourself or buy a new one.