I haven't had to deal with foreign motors much. So I want to bounce off the calculation off of someone else since most of the US motors fit nicely into the NEC 2008 table 430.250.
this motor is a 5.5 HP 460volt 40degree c 1.15 service factor 7.3 nameplate amps. 3 phase AC.
Since there wasn't a 5.5 HP on the table, I used the 5 hp and 1/2 hp and added those full load currents together, 5 hp = 7.6 1/2hp=1.1 7.6+1.1= 8.7 flc
8.7 X 1.25= 10.875 minimum condutor size 8.7X 2.5= 21.75 shortcircuit/ground fault protection
Was it ok to just add the 1/2 hp and 5 hp together that way to get the actual flc since we dont have a 5.5 on our table, maybe Europe has that on their table? I was concerned ,probably for nothing, to be sure the math was right.