motor calc help
furbis
I am taking the colorado journeymans this week and in my studying came across a ? I am unsure of.
"Determine the current of a 10hp motor,208volt, 1 phase, operating at 90% efficiency, with an 85% power factor."
A.46.88 B.50 C. 55 D. 68.75
I am clear on 430.248 for the FLC and 430.22 for 125% but not sure how to figure efficiency and power factor.
Re: motor calc help
First, you need to know that 1 hp = 746 watts. Then, you can convert the hp of the motor to watts:
10*746 = 7460 Watts
But that is output power. To get input power, you need to factor in efficiency:
Pin = Pout/Eff, so
Pin = 7460/.9 = 8289 Watts.
To get current, use the single phase power formula:
P = I*V*Pf
Then solve for current:
I = P/(V*Pf), so
I = 8289/(208*.85) = 46.88 Amps, or answer (A).
:D
Re: motor calc help
thanks I will try and fit that into my brain with all the other stuff I have been studying. :D