I pulled this one from the archives. Thank you Casey(OP who posted this many moons ago):
"1) What size inverse time circuit breaker is required for a
feeder supplying the following motors on a 480 volt three
phase delta system? One 15 hp 480v motor, two 10 hp 480v
motors, and one 75 hp 480v motor @ 15 minute intermittent
duty?
Per table 430.150
15hp 460 = 21A
10hp 460 = 14A
75hp = 96A (430.22 E) 96A * .85 = 81.6A
Per 430.52
81.6A * 2.5 =204A next size up 225A
Per 430.62
225A + 21A + 14A + 14A = 274A next size down 250A
250A inverse time breaker"
I had almost this exact question on my test. My question is does table 430.22(E) even apply to this question? Section II is for sizing conductors. If you are applying 430.62 does 430.22 apply? 430.62 is based off the short circuit rating? Is the 15 minute intermittant part of the question extraneous?
"1) What size inverse time circuit breaker is required for a
feeder supplying the following motors on a 480 volt three
phase delta system? One 15 hp 480v motor, two 10 hp 480v
motors, and one 75 hp 480v motor @ 15 minute intermittent
duty?
Per table 430.150
15hp 460 = 21A
10hp 460 = 14A
75hp = 96A (430.22 E) 96A * .85 = 81.6A
Per 430.52
81.6A * 2.5 =204A next size up 225A
Per 430.62
225A + 21A + 14A + 14A = 274A next size down 250A
250A inverse time breaker"
I had almost this exact question on my test. My question is does table 430.22(E) even apply to this question? Section II is for sizing conductors. If you are applying 430.62 does 430.22 apply? 430.62 is based off the short circuit rating? Is the 15 minute intermittant part of the question extraneous?