Motor Calc.

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
I’m not following how they came up with #1’s MI cable to feed the fire pump. This is 120/208v system and the SP-1 is 208v. 20HP motor @208v is 59.4 amps. The SS-2 disconnect switch is 400A. Not sure how they come up with #1’s to fed the motor.
 

Attachments

  • Capture.JPG
    Capture.JPG
    75 KB · Views: 27
If it's a 400A switch, it may not accept conductors smaller than #1 on its lugs, and someone didn't want to deal with swapping lugs.


SceneryDriver
 
Got it. Could be upsized for VD as texie suggested. Fire pumps are one of the few places in the code where VD compensation is required. How long is the run?
 
If it's a 400A switch, it may not accept conductors smaller than #1 on its lugs, and someone didn't want to deal with swapping lugs.


SceneryDriver
Could be. Looking at Hubbell, a 400A switch will accept #2 to 600MCM lugs! IDK how they did it with #1!
 