Feeder tag 100G referecnes a feeder schedule for #1's.How did you get #1 AWG conductors from that diagram?
Only the feeder OCPD, not the conductors.Fire pump circuits must be rated to handle the locked rotor current of the motor
Yes, I saw that mistake and deleted it, but you caught it first.Only the feeder OCPD, not the conductors.
You know how it is around here. Rough crowd.Yes, I saw that mistake and deleted it, but you caught it first.
Got it. Could be upsized for VD as texie suggested. Fire pumps are one of the few places in the code where VD compensation is required. How long is the run?
Then the conductor size is a little oversized for the application.180'
Could be. Looking at Hubbell, a 400A switch will accept #2 to 600MCM lugs! IDK how they did it with #1!If it's a 400A switch, it may not accept conductors smaller than #1 on its lugs, and someone didn't want to deal with swapping lugs.
SceneryDriver