Am I looking at this right?
Motor HP 22.8 per schedule
Per 430.250 I use 25 HP and it says 74.8 amps. Multiply that by 125% and it gives me 93.5 amps.
Schedule is calling for #2's but #3's would actually be ok??? Figuring what they show but I'm curious.