wannawaterski
Member
This is a question that is similar, if not the same, as a previous question, except I have specifics!
The question is stated as such: There are 6 motors on a 480V, 120/240V delta 3 wire system, served by a single service with the 120/240 loads being served through a transform. What is the load on the service in VA?
Motor #1: 115V, single phase, 2 Hp, continuous duty, nameplate 19.92 A
Motor #2: 115V, single phase, 3 Hp, intermittent duty rated at 5 min., nameplate 28.22A
Motor #3: 230V, single phase, 5 Hp, continuous duty, nameplate 23.24A
Motor #4: 460V, 3 phase, 30 Hp, continuous duty, nameplate 33.2A
Motor #5: 460V, 3 phase, 40 Hp, intermittent duty rated at 5 min., nameplate 43.16A
Motor #6: 460V, 3 phase, 50 Hp, continuous duty, nameplate 53.95A
OK, so I know you're supposed to use the tables in Article 430 for the currents. For single phase it's I X E and for 3 phase it's I X E X sq.rt. of 3. Do you use the nameplate voltage (115,230,460) or the input voltage (120,240,480)? Also, I'm not certain if you need to consider the duty rating of the intermittent motors, which I don't think so, and of course, use the largest motor demand at 125%. I assume when you figure the VA of the 115/230V motors, you total them up, regardless of the fact that they are fed through a transformer since there is no mention of a power factor, and then add them to the total of the VA's for the 460V motors.
Believe me, I've tried several different ways to try to get an answer that was even close to what they offer for choices, and I'm completly frustrated. HELP ME PLEASE SOMEONE!!!!!
The question is stated as such: There are 6 motors on a 480V, 120/240V delta 3 wire system, served by a single service with the 120/240 loads being served through a transform. What is the load on the service in VA?
Motor #1: 115V, single phase, 2 Hp, continuous duty, nameplate 19.92 A
Motor #2: 115V, single phase, 3 Hp, intermittent duty rated at 5 min., nameplate 28.22A
Motor #3: 230V, single phase, 5 Hp, continuous duty, nameplate 23.24A
Motor #4: 460V, 3 phase, 30 Hp, continuous duty, nameplate 33.2A
Motor #5: 460V, 3 phase, 40 Hp, intermittent duty rated at 5 min., nameplate 43.16A
Motor #6: 460V, 3 phase, 50 Hp, continuous duty, nameplate 53.95A
OK, so I know you're supposed to use the tables in Article 430 for the currents. For single phase it's I X E and for 3 phase it's I X E X sq.rt. of 3. Do you use the nameplate voltage (115,230,460) or the input voltage (120,240,480)? Also, I'm not certain if you need to consider the duty rating of the intermittent motors, which I don't think so, and of course, use the largest motor demand at 125%. I assume when you figure the VA of the 115/230V motors, you total them up, regardless of the fact that they are fed through a transformer since there is no mention of a power factor, and then add them to the total of the VA's for the 460V motors.
Believe me, I've tried several different ways to try to get an answer that was even close to what they offer for choices, and I'm completly frustrated. HELP ME PLEASE SOMEONE!!!!!