joe j
Member
- Location
- pittsburgh pa
What minimum size THWN cu conductors are required to supply a continuous duty 25 hp, 208 v, 3 phase motor? The motor is on the end of a short conduit run that contains only 3 conductors at an ambient temp of 50 deg. C. Consider the motor terminations to be rated for 75 deg.C. Full load current rating of the motor is 74.5 amps from table 410.250 and as per 410.22 multiply by 125% =93.5 amps. The temp correction factor found in 310.15(B)(2)(a)is 0.75 -------MY question is do you divide by the temp correction factor and why?