430.6 Ampacity and Motor Rating Determination. The size of
conductors supplying equipment covered by Article 430 shall
be selected from the allowable ampacity tables in accordance
with 310.15(B) or shall be calculated in accordance with
310.15(C). Where flexible cord is used, the size of the conductor
shall be selected in accordance with 400.5. The required
ampacity and motor ratings shall be determined as specified in
430.6(A), (B), (C), and (D).
(A) General Motor Applications. For general motor applications,
current ratings shall be determined based on (A)(1) and
(A)(2).
(1) Table Values. Other than for motors built for low speeds
(less than 1200 RPM) or high torques, and for multispeed
motors, the values given in Table 430.247, Table 430.248,
Table 430.249, and Table 430.250 shall be used to determine
the ampacity of conductors or ampere ratings of switches,
branch-circuit short-circuit and ground-fault protection,
instead of the actual current rating marked on the motor
nameplate. Where a motor is marked in amperes, but not
horsepower, the horsepower rating shall be assumed to be that
corresponding to the value given in Table 430.247