Got specs for some equipment that I have to supply wiring and disconnect for.
Manufacturer sent us the following: "Booster pump 3HP 230V/3 Phase @ 9.6 Amps (230V 1 Phase @ 34 Amps)" and Backwash pump 5HP 230V/3 Phase @ 15.2A ( 230V 1 Phase @ 54A)"
I believe those figures to be wrong. I've calc'd it many times and I have 17A @ 1 Phase for the 3HP and 28A @230V for the 5HP. I have assumed a PF of .80 on my calcs.
Have I done my calculations wrong?
I believe they did the single phase calcs based on 115V, not 230. But before I question an engineer, I want to make very sure.
Manufacturer sent us the following: "Booster pump 3HP 230V/3 Phase @ 9.6 Amps (230V 1 Phase @ 34 Amps)" and Backwash pump 5HP 230V/3 Phase @ 15.2A ( 230V 1 Phase @ 54A)"
I believe those figures to be wrong. I've calc'd it many times and I have 17A @ 1 Phase for the 3HP and 28A @230V for the 5HP. I have assumed a PF of .80 on my calcs.
Have I done my calculations wrong?
I believe they did the single phase calcs based on 115V, not 230. But before I question an engineer, I want to make very sure.