I'm working on a motor calculation that I can't seem to get the right answer for. I think I am working it out correctly, and finally grasping the conception of how to do one, but frustrated because the answer I am getting seems to not be right.
Here's the question:
What size RHW aluminum conductor would be required for 4 - 230 volt 3-phase motors rated: 1 - 7 1/2 hp, 1 - 5hp, and 2 @ 25 hp?
My Math:
Full Load current amps for the following motors.
7 1/2HP - 22A
5hp -15.2 A
25hp - 68A
25hp - 68 A
I then took the 125% of the 68A and got 85 A.
Then I did the following math:
85+22+15.2+68=190.2A
Since you can round up to the nearest next fuse size - that is 200A
Looking at T310.16 in the AL column I get 250kcmil.
The Actual answer says 350kcmil. What did I forget to do?
I am not sure if the answer that I had provided is wrong, or if my math was wrong. I checked this with my dad and he also came up with 250 kcmil.
Here's the question:
What size RHW aluminum conductor would be required for 4 - 230 volt 3-phase motors rated: 1 - 7 1/2 hp, 1 - 5hp, and 2 @ 25 hp?
My Math:
Full Load current amps for the following motors.
7 1/2HP - 22A
5hp -15.2 A
25hp - 68A
25hp - 68 A
I then took the 125% of the 68A and got 85 A.
Then I did the following math:
85+22+15.2+68=190.2A
Since you can round up to the nearest next fuse size - that is 200A
Looking at T310.16 in the AL column I get 250kcmil.
The Actual answer says 350kcmil. What did I forget to do?
I am not sure if the answer that I had provided is wrong, or if my math was wrong. I checked this with my dad and he also came up with 250 kcmil.