Since the equipment grounding conductor is based on the size of overcurrent protection device. Lets say the inverse time breaker on a 30 amp FLA continuous load motor is 30x 250% = 75 amp so we will use a 80 OCP.
circuit ampacity would be 30 x 125%= 37.5 so we will use # 8 wire size.
My question is do I size the equipment grounding conductor 40 amps(#10) from table 250.122 or 80 amp (#8 ) from same table?
circuit ampacity would be 30 x 125%= 37.5 so we will use # 8 wire size.
My question is do I size the equipment grounding conductor 40 amps(#10) from table 250.122 or 80 amp (#8 ) from same table?